Charlie,

I can't seem to find the procedure in part 9 of the 13th edition AISC Manual
that checks for adequate flexibility in the thickness of the angles in
double angle shear connections. Under the "Rotational Ductility" section on pg 9-13, there is a procedure to check for rotational ductility in tee shear
connection although, it only sizes the welds, bolts, and stem of the tee,
not the flange of the tee which is the dimension associated with prying vs.
flexibility issue.  Other than that, I can't find any other procedure
associated with flexibility in a simple connection.


Best regards,


Kyle DeLabar, EIT
LVTA
Lehigh Valley Technical Associates, Inc.
Ph: 610-262-6345
Fax: 610-262-8188

----- Original Message -----
From: "Carter, Charlie" <carter(--nospam--at)aisc.org>
To: <seaint(--nospam--at)seaint.org>
Sent: Thursday, March 23, 2006 12:57 PM
Subject: RE: Tension load on AISC Framed Beam Connection


Rand Holtham wrote:
When determining the adequacy of an AISC standard double
clip angle (framed beam) connections....is prying action
due to axial tension considered as in hanger-type
connections as in 4-89 (AISC ASD-89) or is this
mixing apples and oranges.

Yes, when a tension load is present, prying action applies to the design
of double angles. But, there is then the concern that the angles sized
for the tension load and prying action should not get too thick for the
gage such that they will no longer be able to flex to accommodate the
simple beam rotation.

If you are using the workable gages listed in the AISC Manual and the
angle thickness does not exceed 5/8 in., the angles are still flexible
enough. If you have thicker angles or different gages, you can check
that adequate flexibility exists with procedures given in Part 9 of the
13th Edition AISC Manual. These procedures are the same ones used to
justify the 5/8 in. for the workable gages we list.

Charlie

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
*   This email was sent to you via Structural Engineers
*   Association of Southern California (SEAOSC) server. To
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
*   send to the list is public domain and may be re-posted
*   without your permission. Make sure you visit our web
*   site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********



******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* * This email was sent to you via Structural Engineers * Association of Southern California (SEAOSC) server. To * subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
* Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you * send to the list is public domain and may be re-posted * without your permission. Make sure you visit our web * site at: http://www.seaint.org ******* ****** ****** ****** ******* ****** ****** ********