RE: IBC Fire Walls and Seismic Code

[Subject Prev][Subject Next][Thread Prev][Thread Next]
In my neck of the woods we call that a "fusible link" and I typically use Nylatron bolts. Heckmann also sells a metal break away connection but I prefer the Nylatron because it "melts" at a substantially lower temperature (500 degrees) than the Heckmann connectors.
 
Matthew

________________________________

From: Kestner, James W. [mailto:jkestner(--nospam--at)somervilleinc.com]
Sent: Wed 4/26/2006 5:35 PM
To: seaint(--nospam--at)seaint.org
Subject: RE: IBC Fire Walls and Seismic Code


Matthew:
 
That is correct. For double walls, the required space is between each wall.
 
Weak link is a type of fastening detail that will release the firewall from the structure undergoing a fire condition. 
 
Jim K.
 
  
 -----Original Message-----
From: Stuart, Matthew [mailto:mstuart(--nospam--at)schoordepalma.com]
Sent: Wednesday, April 26, 2006 2:54 PM
To: seaint(--nospam--at)seaint.org
Subject: RE: IBC Fire Walls and Seismic Code



	For double fire walls the "space" for movement occurs between the two adjacent walls and not between the steel and the wall as is the case for the most part with the other examples.
	 
	I'm not familiar with the term "Weak Link", what does this mean?
	 
	Matthew Stuart

________________________________

	From: Kestner, James W. [mailto:jkestner(--nospam--at)somervilleinc.com]
	Sent: Wed 4/26/2006 4:11 PM
	To: seaint(--nospam--at)seaint.org
	Subject: RE: IBC Fire Walls and Seismic Code
	
	
	There are several ways to design firewalls:
	 
	Cantlivered
	Tied
	Double
	Weak Link
	 
	With steel structures, you must provide enough distance between structures for the steel to expand without damaging the firewall(s). This distance varies 2 1/2" and 7 1/2".
	 
	I would think that the double firewall or tied firewall would be the common way to design in seismic areas.
	 
	The IBC gives little guidance to the engineer on how to design these firewalls. The best references are NFPA 221, FM, NCMA and Commentary M of the Canadian Code.
	 
	Jim K.

		-----Original Message-----
		From: Paul Feather [mailto:pfeather(--nospam--at)SE-Solutions.net]
		Sent: Wednesday, April 26, 2006 2:00 PM
		To: SEAOC List
		Subject: IBC Fire Walls and Seismic Code
		
		
		Under the IBC, the area separation walls from the UBC are gone, and the corresponding wall is a Fire Wall.
		 
		The primary difference is the ability of one side of the structure to collapse, without taking down the wall.  The commentary clearly shows the diaphragm sheathing as discontinuous at the Fire Wall in Type V construction.
		 
		Question, how does this square with the seismic code provisions where all parts of the structure are to be interconnected, or a separation joint is to be provided?  Are we now supposed to provide 4 to 8 inch seismic joints at all area separation walls, essentially breaking the building into multiple buildings?  
		 
		Under the UBC Area Separation Walls it was permissible to have the sheathing extend through at the floor diaphragms, and the only problem was maintaining the rating through the assembly.
		 
		What are other people doing about this condition?  
		 