Could you consider  this condition similar to a concentrated load on a corbel and analyze and reinforce it per ACI 11.9?

 

Bob Garner, S.E.

 


From: Mike Zaitz [mailto:mzaitz(--nospam--at)hgbd.com]
Sent: Monday, July 17, 2006 4:44 AM
To: seaint(--nospam--at)seaint.org
Subject: Concentrated Load at Edge of Pedestal

 

I have a condition where I will have concentrated loads near the edge of the concrete pedestal under some latticed columns.  The pedestal is 4'-0" x 2'-0" with 2-W14x43 columns with the webs parallel to the short dimension.  The centerlines (parallel to the web) are only 5 inches from the edge.  For this case my factored load is only 157 kips but on other areas they will be higher.  I have checked the bearing for the concrete and am trying to find anything for verifying that I will not spall the edge of the pedestal.  I do not find anything in the code (ACI 318-99) that addresses this condition (other than the concrete bearing).  Is there something I am missing?

The information contained in the e-Mail, including any accompanying documents or attachments, is from Moffatt & Nichol and is intended only for the use of the individual or entity named above, and is privileged and confidential. If you are not the intended recipient, be aware that any disclosure, dissemination, distribution, copying or use of the contents of this message is strictly prohibited. If you received this message in error, please notify us.