Mike,
 
I am not sure if I understand your problem.  The bearing pressure under the baseplate is easily calculated, and then compared to the one available from the pedestal.  ACI formulas are quite old, and proven to work for small and large pedestals, high and low loads.  For example, look at ACI318 Section 10.17 and Fig. 10.17 - if this is your case, you are going to be OK by checking the bearing pressure.
 
According to PCI "Notes on ACI318", reinforcement to "transfer excess loads" "must be provided" "when the bearing strength is exceeded."  In order to have this condition, thought, you have to have something really exotic going on.
 
Steve Gordin SE
Irvine CA
 
On Mon, 17 Jul 2006, Mike Zaitz wrote:

> I have a condition where I will have concentrated loads near the edge of the
> concrete pedestal under some latticed columns.  The pedestal is 4'-0" x
> 2'-0" with 2-W14x43 columns with the webs parallel to the short dimension.
> The centerlines (parallel to the web) are only 5 inches from the edge.  For
> this case my factored load is only 157 kips but on other areas they will be
> higher.  I have checked the bearing for the concrete and am trying to find
> anything for verifying that I will not spall the edge of the pedestal.  I do
> not find anything in the code (ACI 318-99) that addresses this condition
> (other than the concrete bearing).  Is there something I am missing?
>

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
*   This email was sent to you via Structural Engineers
*   Association of Southern California (SEAOSC) server. To
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org . Remember, any email you
*   send to the list is public domain and may be re-posted
*   without your permission. Make sure you visit our web
*   site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********