Rich.
I have the Butler foundation manual. It looks a little dated, but the info is good. I think that Butler or somebody who wants to promote better foundations for PEMB's should
undertake to up-date it - I don't think it is a lot of work.
Up here, we have have 4' of earth for frost protection. Consequently we have higher overturning moments and usually the footing ends up being rectangular with the long dimension parallel to the frame. It can be problem up against existing buildings. Also avoid hair-pins and tie-rods. They get removed in later renovations or in my case before the building was completed; the Owner was digging into the sub-base to install service trenches for equipment and cutting the rebar. When I asked him about it, he shrugged and said he forgot about them. Tie-bars are the same problem but also can be a big hassle to install. Just design bigger footings- they have to pour the concrete anyway so just pour more.
Gary

jvhannah wrote:
To: Rich Lewis
You need to contact a Butler Builder, i.e. a contractor who sells Butler Manufacturing Company buildings. The Butler manual is available to them. It is not being printed or updated. They need to go on the private Butler Web site (www.mybuildernet.com <http://www.mybuildernet.com>) and they have to login to an already existing Butler account and they can purchase one of the remaining copies. I don't know how many exist. Butler is selling them for $15. They were written by Computerized Structural Design out of Milwaukee, WI by Dr James Fisher, PE among others. (spelling and titles by my memory). Also there is another book Metal Building Systems : Design And Specifications <http://www.abebooks.com/servlet/BookDetailsPL?bi=791979265&searchurl=bx%3Doff%26sts%3Dt%26ds%3D30%26bi%3D0%26y%3D12%26kn%3Dmbma%26tn%3Dmetal%2Bbuildings%26x%3D64%26sortby%3D2> (ISBN: 0071402012 <http://www.abebooks.com/servlet/BookDetailsPL?bi=791979265&searchurl=bx%3Doff%26sts%3Dt%26ds%3D30%26bi%3D0%26y%3D12%26kn%3Dmbma%26tn%3Dmetal%2Bbuildings%26x%3D64%26sortby%3D2>)* *by Alexander Newman, which devotes some space to pemb foundations. He also gives seminars on the design of pemb foundations thru the ASCE. If I understand what you said in your question, you are not using piers and a footing pad??? You are using a thickened edge slab??? Are you located in an area with low frost penetration or are you using insulation to control frost heaving??? It sounds like you are not using a pad footing to support your column loads. We are normally down at least 48" so we some moment (sometimes considerable). Due to that moment our long dimension, if there is one, is usually parallel to plane of the frame.
I am looking forward to more comment on this issue.
Jim Hannah

    ----- Original Message -----
    *From:* Rich Lewis <mailto:seaint04(--nospam--at)lewisengineering.com>
    *To:* seaint(--nospam--at)seaint.org <mailto:seaint(--nospam--at)seaint.org>
    *Sent:* Wednesday, October 11, 2006 8:17 PM
    *Subject:* PEMB Column Footing

    I’m looking for insight in the design of Pre-Engineered Metal
    Building column footing. I’m not sure if anyone can give me any
    insight or not beyond what I already know. I’ve already designed
    dozens of these systems. I’m looking for a ‘better way’. Maybe
    there are some tricks to the trade that I’m not aware of. I really
    can’t find much information on the design of these foundations in
    print. I have seen a little blurb in the MBMA system design
    manual. It is not of much help.

    I typically design foundations for PEMB as turned down perimeter
    slab systems. At the rigid frame columns a footing is created
    below the frame. I always try to get the column inside the
    perimeter grade beam. If I have a heavy crane loaded column this
    usually can’t be done and the column footing is center and below
    the perimeter grade beam. I design the footing as an eccentrically
    loaded footing. I add dead weight from the surrounding slab and
    grade beams to help resist wind uplift forces. I’m always finding
    myself fighting the eccentric loads on the soil bearing pressure,
    especially on projects with inset wall girts. On those projects
    the column load is less than a foot from the edge of footing and
    the soil bearing stresses shoot sky high. I usually end up with
    rectangular size footing with the long dimension parallel to the
    perimeter wall.

    From my perspective, this is the correct way to design the
    footing, but maybe my perspective is not inclusive enough. Are
    there ‘numbers games’ that can be made to reduce the eccentricity,
    which in turn distributes the stresses more evenly under the
    footing? I can’t picture any. I use hairpins and tie rods, but I
    see these as only being ‘equal and opposite’ to the rigid frame
    thrust. I can’t see how these would help induce any loads to
    reduce the physical eccentricity of the column on the footing.

    Are there other methods of analysis out there others use to get
    more reasonable footing design below rigid frames? Does anyone
    know of literature that addresses these types of foundations in a
    comprehensive way? I understand there is an old Butler design
    manual but it is out of print and I haven’t been able to see a copy.

    Thanks for any insight.

    Rich


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* * This email was sent to you via Structural Engineers * Association of Southern California (SEAOSC) server. To * subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
* Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you * send to the list is public domain and may be re-posted * without your permission. Make sure you visit our web * site at: http://www.seaint.org ******* ****** ****** ****** ******* ****** ****** ********