Kevin:

For hollowcore planks:

Per my Spancrete literature (which is kind of dated, but still should be
fine), a 6" to 12" plank with a strand cover of 1.25" will have an
unrestrained fire rating of 1 hour per UL J982.  Going to 2" of cover gets
you 2 hours of unreinstrained fire rating per UL J959.  UL J925 gets you
1.5 hours (unrestrained) or 2 hours (restrained) with 1.5" of cover and UL
J924 gets you 1 hour (unrestrained) or 4 hours (restrained) with 1.5" of cover.

If you want general guidance, then you can take a look at the PCI Design
Handbook.  It does not give direct fire ratings, but has a section on fire
ratings of precast concrete that could be used to analytically come up
with something.

For concrete on metal deck:

You can get a 1 hour rating out of 3.5" NW concrete above the flutes or
2.5" LW concrete above the flutes with composite deck using a variety of
UL Design Numbers (i.e. different numbers relate to slightly different
configurations...you would need a UL book for figure out what the EXACT
configuration is for the UL #).

HTH,

Scott
Adrian, MI

On Mon, 16 Oct 2006 David.Topete(--nospam--at)wildman-morris.com wrote:

> Kevin,
> See the literature for the different manufacturers of steel deck and
> precast planks.  I typically call out Verco decking.  (ICBO ER-2078P)  You
> get a 2 hour fire rating from a 3" metal deck with 3-1/4" ltwt concrete
> fill.
> For the hollow core planks, we spec'd out planks by Hanson Spancrete.  We
> have an old catalog fo theirs, but they list the fire ratings based on the
> concrete cover to the prestressing strands.  On one project we needed 12"
> ltwt hollow core planks with a 3-1/2" nw conc topping, and that gave 2
> hours (I believe...).
> HTH.
> David A. Topete, S.E.
>
> Wildman & Morris
> 120 Howard Street, Suite 500
> San Francisco, CA 94105
> P:   (415) 896-2644
> F:   (415) 896-2636
> David.Topete(--nospam--at)wildman-morris.com
>
>
>
> "Kevin Below" <kbelow(--nospam--at)genio.ca>
> 10/16/2006 03:10 PM
> Please respond to
> <seaint(--nospam--at)seaint.org>
>
>
> To
> <seaint(--nospam--at)seaint.org>
> cc
>
> Subject
> Fire rating of steel deck floor and hollow-core slabs.
>
>
>
>
>
>
> I can't find Canadian code reference for the fire rating of a steel deck
> with concrete.
> I need a 1 hour separation.  The architect says he thinks that we can
> avoid spraying fireproofing on the steel deck underside if the concrete
> thickness is increased.
> (We would spray the joists and beams only).
> Can anyone point me in the right direction ?
>
> Supplementary question:
> We are also considering hollow-core slabs.  All spans are 25 feet, and 8"
> slabs with a 2" topping seem appropriate.  Anyone have experience with
> these ?  Any nightmares to be avoided ?
>
>
>
> Kevin Below
>
>

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********