Thanks, Will, for the response.  In the situation I have, the span between shearwalls in either direction is not too bad.  I can reasonably assume the waffle grid is stiff enough to be considered “rigid.”

David Topete, SE

 


From: Will Haynes [mailto:gtg740p(--nospam--at)gmail.com]
Sent: Thursday, December 14, 2006 4:53 PM
To: seaint(--nospam--at)seaint.org
Subject: Re: 2-in conc slab = rigid diaph?

 

ACI 2002 section 21.9.4 gives 2" as the minimum required for a diaphragm. I am not sure if it can automatically be considered rigid.

 

 

Will Haynes

 

On 12/14/06, David Topete <dtopete(--nospam--at)gfdseng.com> wrote:

I am doing a peer review.  The structures are masonry, single story.  Some have pitched roofs.  Others are flat roofs.  The flat roofs are made of a c.i.p. concrete waffle grid, 8" joists, 2 feet c.c. each way in a 12" deep system.  The slab itself is only 2-in thick with 6x6 wire mesh reinforcement.  Can I assume the slab itself as essentially zero, and depend on the grid for diaphragm action to transfer loads to the LFRS?  If anyone has a quick answer, it'd be most appreciated.

 

David A. Topete, SE

Structural Engineer

 

GFDS Engineers

543 Howard St., First Floor

San Francisco, CA 94105

v : (415) 512-1301 x21

f : (415) 512-1302

dtopete(--nospam--at)gfdseng.com

http://www.gfdseng.com