Also look in Chapter 16 of the UBC.  I believe that there is a provision
in the UBC (I know it is in the IBC, but don't have my UBC with me) that
bascially says that if you change the seismic loading to an existing
element by 5%, then it has to be re-evaluated and potentially reinforced
in needed...or something to that effect (don't recall exactly what it
says).

As to references for design of partially grouted CMU walls...

You might try the Masonry Designer's Guide from TMS
(www.masonrysociety.org).  It is a rather decent practical guide for
masonry design.  The 4th edition is per the 2002 MSJC (masonry code).
Since the 1997 UBC is nominally similar to the 1995 MSJC and/or the 1999
MSJC (but the UBC has strength design while those two codes do not), you
might see if you can get the 3rd edition still (based upon 1999 MSJC).  It
really should not matter, however, as the basics of ASD in masonry have
remained largely unchanged.

Regards,

Scott
Adrian, MI


On Fri, 12 Jan 2007, Gerard Madden, SE wrote:

> Check with the building official. If it's in the bay area, my experience has
> been 5% increase in demand load or 5% reduction in capacity triggers full
> compliance of those elements with current code.
>
> Change in occupancy would trigger full upgrade of the entire structure.
>
> -g
>
> On 1/12/07, David Topete <dtopete(--nospam--at)gfdseng.com> wrote:
> >
> >  G-
> >
> >
> >
> > Would that be necessary even without a "Change of Use?"  The space is a
> > supermarket, and they are acquiring adjacent space, and making penetrations
> > in a common wall.  The openings are okay in the common concrete wall.  It's
> > the storefront wall that is in question.  Modifying the storefront wall
> > means I have to check for '01 CBC seismic.  But, if the partial grout wall
> > works, I should be okay.  Am I interpreting that wrong?
> >
> > The wall ties are not an issue.
> >
> > Thanks.
> >
> >
> >
> > *David A. Topete, SE*
> >
> > Structural Engineer
> >
> >
> >  ------------------------------
> >
> > *From:* Gerard Madden, SE [mailto:gmse4603(--nospam--at)gmail.com]
> > *Sent:* Friday, January 12, 2007 4:42 PM
> > *To:* seaint(--nospam--at)seaint.org
> > *Subject:* Re: Partial grout CMU shear wall
> >
> >
> >
> > Zone 4? You'll need full grout and meet wall anchorage mins on the
> > existing walls if you're increasing the load to these guys by 5% or more due
> > to the addition...
> >
> > -g
> >
> > On 1/12/07, *David Topete* <dtopete(--nospam--at)gfdseng.com> wrote:
> >
> > Yup.  "They" make California a tough lace to make a living, or a
> > building.  Thanks for the info, Will.
> >
> >
> >
> > *David A. Topete, SE*
> >
> > Structural Engineer
> >
> >
> >  ------------------------------
> >
> > *From:* Will Haynes [mailto:gtg740p(--nospam--at)gmail.com]
> > *Sent:* Friday, January 12, 2007 4:02 PM
> > *To:* seaint(--nospam--at)seaint.org
> > *Subject:* Re: Partial grout CMU shear wall
> >
> >
> >
> > I use partial grouted walls walls all the time in my area. I heard
> > California requires fully grouted?
> >
> >
> >
> > Here is one basic reference I have used before:
> >
> > http://www.usace.army.mil/publications/armytm/tm5-809-3/chap5.pdf
> >
> >
> >
> > The rest:
> >
> > http://www.usace.army.mil/publications/armytm/tm5-809-3/
> >
> >
> >
> > Will
> >
> >
> >
> > On 1/12/07, *David Topete* <dtopete(--nospam--at)gfdseng.com> wrote:
> >
> > I'm analyzing and designing for a supermarket that's enlarging, and has
> > been added on over the years.  A lot like the Winchester Mystery House in
> > San Jose.  Original construction is 6" concrete tilt-up.  Addition 1 was
> > partial grout masonry, 30yrs ago.  Addition 2 was an extension on Add'n 1,
> > and partial grout CMU as well.  Is there a reference out there for analysis
> > and/or design of partial grout masonry?  This is hollow concrete block with
> > bond beams at 48"o/c max., and vertical steel at 32" or 48"o/c.  Any help is
> > much appreciated.
> >
> >
> >
> > *David A. Topete, SE*
> >
> > Structural Engineer
> >
> >
> >
> > GFDS Engineers
> >
> > 543 Howard St., First Floor
> >
> > San Francisco, CA 94105
> >
> > v : (415) 512-1301 x21
> >
> > f : (415) 512-1302
> >
> > dtopete(--nospam--at)gfdseng.com
> >
> > www.gfdseng.com
> >
> >
> >
> >
> >
> >
> >
> >
> > --
> > -gm
> >
>
>
>
> --
> -gm
>

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********