David,

I assume based upon your description that the cracks basically occur at
the masonry mortar joints primarily (i.e. based upon your conclusion of
thermal effects...presumably thermal effects of the precast t-beam).  Is
that the case or do you have significant cracking of the CMU units
themselves?  Is the cracking/movement causing CMU blocks to basically move
out-of-plane (i.e. pull out from the wall)?  If the later is true, then I
could see some concerns of continuous bearing of the units at the bed
joints at the faces of the units (might be only down to bearing at the
webs if two successive courses don't line up).

I would say that if the "bearing" of the face bed joints is still
basically good and it is just a matter of some mortart joints opening up,
then using mortar might be OK.  But, I can't get a good feel for how bad
things may or may not be from your description.  I would say that the
biggest issue may not be the repair of the cracks, but rather has the
masonry lost enough structural integrity (i.e. out of plum or blocks no
longer sitting directly on top of each other or "buckling" of the the CMU)
to have general structural problems.  If the wall is stabile and doesn't
have any serious overall structural deficiencies, then mortaring the
cracks might be Ok.

Regards,

Scott
Adrian, MI

On Fri, 12 Jan 2007, M. David Finley, P.E., P.A. wrote:

> Old pedestrian bridge consisting of single web precast t-beam.  60'-0" span.
> Abutments are rectangular (8'-0" wide to match the t-beam and 6'-0" long).
> The front (bridge side) wall bears on a concrete gravity wall.  The side
> walls bear partly on the gravity wall and partly on a continuous strip
> footing.  The rear wall is on a strip footing.  All of the masonry is
> 8"x8"x16 CMU with no vertical or horizontal reinforcing and no grouted
> cells.
>
> The masonry in the abutments has cracks, including some with in/out of plane
> displacement.  The cracks appear to be caused by the fact that the original
> construction apparently ignored thermal effects and "locked" both ends of
> the single web t-beam into the front masonry wall.
>
> I am correcting the expansion issue by providing expansion joints at each
> end of the bridge.  No problem there.  And the new expansion joints will
> significantly reduce the forces being transferred into the masonry.
>
> The Owner (small town, so limited funds) wants to repair the masonry by
> patching the cracks with mortar.  Some of the cracks are 3/4" wide.  Can
> cracks that wide be adequately repaired with mortar?  Or should some type of
> pressure epoxy grouting be used?
>
> Of course this bridge has historical significance, so the "tear down and
> replace" option is not available.
> David Finley
> M. David Finley, P.E., P.A.
> 2086 SW Main Boulevard - Suite 111
> Lake City, FL  32025
> 386-752-6400
>
>

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********