Jim,

What you describe is a Structural Insulated Panel (SIP) system.  I happen
to work in the "SIP world", although I deal with wood based SIP panels
(OSB skins glued to EPS foam is the typical application).

At this time, wood based SIPs are tested/evaluated per ICC's Acceptance
Criteria AC04.  I believe that AC04 would potentially apply to concrete
based SIPs as well, but not completely sure.  In particular, it is
Appendix A that is to be used to evaluate SIPs for using in "high seismic"
areas (Seismic Design Categories D, E, and F).  There are two problems
though that might not make it too useful: 1) ICC-ES has decided that there
are still "issues" with Appendix A and as a result, they are going to
modify Appendix A (which is frustrating for the SIP industry because it
has taken a while to get to this point and some have done rather
significant testing per Appendix A including the company that I work
part-time for...but then it was some of this testing that brought to light
some of the issues); and 2) Appendix A was written with an eye toward wood
based SIPs, so I am not sure if ICC-ES intends for it to be used with
concrete based SIPs or not (it does appear to be written in such a generic
way that it potentially could, assuming that you can find an "equivalent"
system to do for the "matched" test similar to doing stick-framed tests
for wood based SIPs).

Regardless, more than like the loading protocol that is used in AC04 would
likely be required for shearwall tests of concrete based SIPs even if AC04
is not used since it is a rather "general" seismic based loading protocol
(i.e. number of cycles, drift limits, etc).  It is SEAOSC's "Standard
Method of Cyclic (Reversed) Test for Shear Resistance of Framed Wall for
Buildings".  It was basically taken over by ASTM as ASTM E2126, but has
changed somewhat from what SEAOSC has.  It is also mainly aimed at wood
based shearwalls, but does have a loading protocol that could be used for
cyclic testing of other walls.

I see that others have pointed you to some folks that specifically have
dealt some with this issue.  You might also contact SIPA, the trade group
for SIPs (www.sips.org).

HTH,

Scott
Adrian, MI


On Mon, 12 Mar 2007, Jim Chatterley PE wrote:

> Gentlemen,
>     I anticipate bidding on a DESIGN-BUILD project that will be constructed
> using a bearing wall sandwich panels for a 4 level apartment building.
> The typical sandwich panel bearing wall is constructed from an inner core of
> 4 inch thick Expanded Polystyrene Foam.  The veneer on both sides of the
> wall is 2 inch thick 2500 +/- PSI shotcrete applied concrete.  The concrete
> veneer is reinforced by a 3 dimensional matrix of 2 x 2 inch wire mesh and
> wire truss assembly.
>     I anticipate the requirement for a racking shear testing under the
> administration of an ICC certified testing laboratory.  Is there a published
> ASTM, ICC Acceptance Criteria, or ACI committee protocol that describes an
> acceptable testing procedure for :
> *  Racking  In-plain Shear testing for concrete shear walls?
> *  Aspect Ratio (minimum height to width dimensions of the tested walls)?
> *  Cycle time of the racking forces?
> *  Number and amplitude of the cycle forces?
>     Any experienced testing guidance will be appreciated.
> Thanks,
> Jim L. Chatterley PE
> Composite Framing Systems, Inc.
> 2723 Currier Ave., Simi Valley, California, 93065
> 805-520-3666   Fax 805-583-1434
> www.Compositeframingsystems.com
>
>
>

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********