How are you framing the platform?
 
You can weld the plate to each framing member and analyze it as supported on four side.
 
Walking vibration is not a large concern to workers using access platforms. Sidesway is.
 
Bill


From: William.Sherman(--nospam--at)CH2M.com [mailto:William.Sherman(--nospam--at)CH2M.com]
Sent: Wednesday, March 14, 2007 8:03 AM
To: seaint(--nospam--at)seaint.org
Subject: RE: Steel floor plate

Based on the responses received, I've developed the followng information:

Say span = 4 ft = 48 inches.  Per the AISC deflection controlled tables, a 3/8-in plate can carry 127 psf.  The calculated deflection is 0.48-in. Recommendations have been made to keep the natural frequency above 5 Hz, or better yet above 11 Hz.  So check the natural frequency for a 0.48-in deflection:
 
Use f = (g/d)^0.5/(2*pi) to estimate natural frequency, where:  g = 32.2 ft/s^2 = 386 in/s^2;  d = deflection of beam = 0.48-in;  so natural frequency f = 4.51 Hz, less than 5 Hz.
 
Try grating criteria of 1/4" deflection under 100 psf live load:  for d = 0.25-in, f = 6.25 Hz, greater than 5 hz.
 
If we try for f = 11 Hz, then d(max) = 0.08-in; thus, a much thicker / stiffer plate would be requried - does not appear to be practical.
 
It has been suggested that a 1/4-in plate is suitable for a 4-ft span.  Check deflection and frequency under a 300-lb concentrated load: 
d = 1.53-in, f = 2.53 Hz;  deflection is excessive and frequency is too low.  
 
Check the 1/4-in plate for a two-way simply supported span under a uniform load of 100 psf: 
d = 0.36-in, f = 5.20 Hz;  meets 5 Hz frequency. 
 
If plate is continuous vs simply supported, the 1/4-in plate is reasonable for 4-ft span each way, but a 1/4-in plate does not appear to be good for a simple span of 4-ft.
 
In my opinion, the 1/4-in maximum deflection under a 100 psf live load appears to provide an easy criterion with reasonable results.
 

From: William.Sherman(--nospam--at)CH2M.com [mailto:William.Sherman(--nospam--at)CH2M.com]
Sent: Monday, March 12, 2007 6:31 AM
To: seaint(--nospam--at)seaint.org
Subject: RE: Steel floor plate

Actually my application "is" an industrial application - the plate will be used at a platform to be used regularly to access equipment.  I don't want the floor plate to feel excessively "bouncy", so I am trying to establish the criteria to use for deflection.  And I will need to justify this criteria to other reviewers.  It is not clear to me whether AISC's "deflection-controlled" table will accomplish this goal. 
 
I currently plan to use criteria consistent with grating design based on historical practice.  However, this platform is movable, so we want to minimize its weight.  If I can justify less stringent criteria, then I could reduce the weight.
 
 
Bill Sherman
CH2M HILL / DEN
720-286-2792
 


From: Scott, William N [mailto:William.N.Scott(--nospam--at)conocophillips.com]
Sent: Thursday, March 08, 2007 9:46 AM
To: seaint(--nospam--at)seaint.org
Subject: RE: Steel floor plate

Bill,
 
The deflection limit applies to industrial applications where deflection does not affect serviceability.
 
Use a lower limit when deemed necessary.
 
Bill


From: William.Sherman(--nospam--at)CH2M.com [mailto:William.Sherman(--nospam--at)CH2M.com]
Sent: Thursday, March 08, 2007 7:36 AM
To: seaint(--nospam--at)seaint.org
Subject: Steel floor plate

Table 3-18a in the AISC 13th Edition provides tabulated allowable uniform loads for "deflection-controlled applications".  The deflection limitation used is L/100.  For a 4-ft span, the maximum deflection would be about 1/2-inch - this seems rather "bouncy" to me.  Grating tables typically recommend a limit of 1/4-inch deflection under 100 psf live load for comfort - but a 3/8-inch plate at a 4-ft span designed per AISC would have about twice that deflection.  
 
What is the basis for the L/100 allowable deflection?  Does this limit provide adequate stiffness for "comfort"?