There has been some good discussion on the maximum deflections of studs that back up brick veneer. There have been many good papers on the topic. Promulgated deflection limits include L/360 (steel stud mfgrs.), L/600 (BIA), and L/720 (Canadian Research).

Interestingly, the BIA guidance (TEK Note 28 B) limits the lateral deflection of the stud to L/600 for "service" wind loads. Per BIA 28B, "Therefore, to obtain sufficient backing stiffness, the allowable out-of-plane deflection of the studs due to service level loads should be restricted to L/600." But BIA does not define "service level loads".

For wind the IBC and ASCE 7 have us calculate the variable "p" that is defined as the "design" wind pressure and is the 50 year Mean Recurrence Interval (MRI). Serviceability is discussed in the ASCE 7 Section C6.5.5 and in the AISC Design Guide 3. The general consensus of the AISC is that service level winds are 10 year MRI winds and are about 75% of the pressure calculated from "design" 50 year MRI winds.

If the above logic is considered valid, the L/600 BIA limit at a "service" 10 year MRI wind would be about the same as a L/400 at a 50 year MRI "design" wind load.

I know it is conservative to use the 50 year MRI for the L/600, but it also increases the cost. I would welcome discussion and any performance studies on systems constructed.

Building codes focus on life safety.  This is a serviceability issue.

Regards,
Harold Sprague

_________________________________________________________________
Find a local pizza place, movie theater, and more?.then map the best route! http://maps.live.com/default.aspx?v=2&ss=yp.bars~yp.pizza~yp.movie%20theater&cp=42.358996~-71.056691&style=r&lvl=13&tilt=-90&dir=0&alt=-1000&scene=950607&encType=1&FORM=MGAC01


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* * This email was sent to you via Structural Engineers * Association of Southern California (SEAOSC) server. To * subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
* Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you * send to the list is public domain and may be re-posted * without your permission. Make sure you visit our web * site at: http://www.seaint.org ******* ****** ****** ****** ******* ****** ****** ********