Bill,
 
ACI 530-05(ASCE,TMS) Section 3.3.4.2.1 "Beams":
 
Members designed primarily to resist flexure shall comply with requirements of Section 3.3.4.2.  The factored axial compressive force on a beam shall not exceed 0.05An f'm.
 
Section 3.3.4.2.3 then states "Transverse Reinforcement shall be provided where Vu exceeds Fi*Vm", and then goes into detailing specs.
 
Let me know if you need more info.
 
V. Steve Gordin, SE
Irvine CA

  
  
 
  
----- Original Message -----
From: Bill Allen
To: Seaint
Sent: Monday, June 02, 2008 14:46
Subject: TMS 402/ASCE 4/ACI 530 Pilaster Question

Are all vertical load supporting elements columns when it comes to masonry?

 

Specifically, I have a 16? square pilaster supporting a trellis. The plan checker considers this element a column and is insisting that I provide ties at 8?. I contend that the pilaster is primarily a flexural member and that fa/F?m is very, very small. I seem to recall this in the concrete section (P<=0.10f?cAg or something like that), but I don?t really see a definition of a column in the masonry section of the code. Of course, I don?t yet have TMS 402, so I?m kind of flying blind.

 

Any clarifications would be appreciated.

 

Regards,

 

T. William (Bill) Allen, S.E.

ALLEN DESIGNS

Consulting Structural Engineers
 
V (949) 248-8588 ? F(949) 209-2509