Bill,

You are right that the ductility issue applies in both tension and shear.  But if you add enough anchors far enough down on the wall, you can get the concrete connection strength of the multiple anchors to be greater than the single threaded rod in tension to the hold down at top of the bracket.  This was an admittedly over-kill design to meet the requirement for a single location, so it was feasible.  I wouldn't recommend it to be used at multiple locations in a retrofit, since it would get real expensive quick.

As far as the series of calcs goes, I ran ACI appendix D calcs in accordance with the ICC ES report for a number of anchor sizes and different "seismically approved" anchors and quickly realized that is was not possible to get the anchors to fail in a ductile manner in tension.  I emailed Hilti tech support since these were the "seismically approved" anchors to see what I was missing.  The tech support provided the following response in May 2007, in the middle of the post-installed anchor crisis:

"You are absolutely right and you are not missing anything. In most of the design cases concrete failure modes are governing and resulting in a brittle failure."

Hilti went on to provide information on the changes approved for ACI 2008 and the 2.5 factor for non-ductile designs.  Combined with the lower values developed under the new testing criteria, this is unfortunately quite a burden on the post-installed anchors and in many cases makes them very difficult to be utilized and meet the direct wording of the code, especially for single anchor bolts or hold downs.  I suspect that in a couple years, Hilti, Simpson and others will find a way to address this issue through new product developments that will meet the intent of the current codes.   In the mean time, I cringe every time I get the call from the contractor with a mis-aligned anchor bolt and the request to pop in a post-installed anchor.

Jared


The ductility issue (1/2.5) not only applies to tension anchors but shear
anchors as well.

Just curious, what "series of calcs" did you go through? Section D.3.3.5
isn't clear on this.

T. William (Bill) Allen, S.E.
ALLEN DESIGNS
Consulting Structural Engineers

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********