We used to hold them separate, but we were called on it on a couple of peer reviews.  We now add the two loads.

 

Looking at example 3 of the “Guide to the Use of the Wind Load Provisions of ASCE 7-02” (granted old code, but it is still the same provisions) the two loads appear to be combined.  As I was taught, windward = pressure, leeward = suction, in the end they act in the same direction.

 

 

Jason Christensen, S.E.

 

Project Engineer

WCA Structural Engineering, Inc.

 

From: Michael Liew [mailto:michaelliew4(--nospam--at)gmail.com]
Sent: Monday, December 08, 2008 3:32 PM
To: seaint(--nospam--at)seaint.org
Subject: Re: ASCE wind on parapets

 

Joe,

 

I use 1.5 for the windward parapet and 1.0 for the leeward parapet.  I don't combine them.

 

Michael Liew

 


 

On Mon, Dec 8, 2008 at 1:35 PM, Joe Goldbronn <jgoldbronn(--nospam--at)barrish.com> wrote:

How are the wind forces on parapets to be applied to the MWFRS (section 6.5.12.2.4)?  Are you to apply both the +1.5*q windward and the -1.0*q leeward pressures onto the same parapet?  This would in essence create a 2.5*q total force on each parapet of a structure.  This seems to be a larger force than I would expect for the parapets which makes me wonder if I am interpreting the code correctly.

 

Joe Goldbronn, PE