RE: ACI 530 R=1.5

[Subject Prev][Subject Next][Thread Prev][Thread Next]
Look at ACI 530 3.1.3.1... it limits the R to 1.5, but only in the strength section.  City of LA code references 530 to answer the other section.
 
I saw 3.3.3.5, and thought thats what they were origianlly referring to, but 3.1.3.1 is pretty clear. But nothing in ASD
 
Rick

--- On Thu, 2/5/09, Paul Feather <PFeather(--nospam--at)se-solutions.net> wrote:
From: Paul Feather <PFeather(--nospam--at)se-solutions.net>
Subject: RE: ACI 530 R=1.5
To: seaint(--nospam--at)seaint.org
Date: Thursday, February 5, 2009, 8:35 AM

ACI 530 does not set or establish R factors.  There are only two possible explanations that I am aware of: first if using strength design there is a provision for maximum area of flexural tensile reinforcement (3.3.3.5) where M/Vd greater or less than 1 and IF the design used an R of less than or greater than 1.5 is a trigger for additional design requirements.  This is not an R factor limitation, just a trigger for other provisions.  Second would be if they are somehow mis-interpreting the shear force required of 1.5V in ASD design, but this is an IBC requirement and not in ACI 530 either.
 
I would ask the Plan reviewer to specify which code provision he / she is referencing with his comment.
 
Paul Feather PE, SE
 
 


From: Rick [mailto:mohr2circle(--nospam--at)yahoo.com]
Sent: Thursday, February 05, 2009 7:58 AM
To: seaint(--nospam--at)seaint.org
Subject: RE: ACI 530 R=1.5

I have a City of LA Plan check comemnt that R = 1.5 "must" be used for masonry walls piers per ACI  530.
 
Can someone point me to the specific reference.