Of course this thread comes the first day of vacation!  I'll try not to get flamed too much here but....

Have you checked out the USP DUC Undercut Anchors in ICC ES ESR 1970?  If I remember correctly, using strength design you should be able to get 12 kips for a 3/4" A36 anchor like the DUC34-500L with a 7 1/2" edge distance, which should work for interior footings.  Probably a little easier than doing the through bolt, at least for the interior!


Howard Silverman, PE
Anchoring Systems and Field Engineer Manager
USP Structural Connectors/Covert Operations
hsilverman(--nospam--at)USPconnectors.com
www.USPconnectors.com

-----Original Message-----
From: Freeman Tang <FTang(--nospam--at)gouvisgroup.com>
To: seaint(--nospam--at)seaint.org
Sent: Thu, 16 Apr 2009 3:56 pm
Subject: RE: ACI 318 Appendix D

Hi Bill,
For interior footings we will try to use post-installed anchors if they work;  however to the best that we can justify these post-installed anchors nowadays ,per Appendix D, can hold up to about 7 kips with 6” edge distance.  Using through-bolts is one of our options if the load goes beyond this magnitude for interior footing.  Off course the concrete slab has to be sawcut or removed before through-bolts can be installed.
 
From: Bill Allen [mailto:t.w.allen(--nospam--at)cox.net]
Sent: Thursday, April 16, 2009 3:21 PM
To: seaint(--nospam--at)seaint.org
Subject: RE: ACI 318 Appendix D
 
Hi, Freeman.
 
I have found that20through bolts aren't very popular at interior shear walls for some reason.
 
:o).
 
Hope all is well.
 
 
T. William (Bill) Allen, S.E.
Consulting Structural Engineers
 
V (949) 248-8588 F(949) 209-2509
-----Original Message-----
From: Freeman Tang [mailto:FTang(--nospam--at)gouvisgroup.com]
Sent: Thursday, April 16, 2009 2:51 PM
To: seaint(--nospam--at)seaint.org
Subject: RE: ACI 318 Appendix D
 
We also use through-bolts for fixing missing holdowns at shear wall ends.  Per Appendix D section 2.2 through bolts are not included.
Freeman Tang
Gouvis Engineering
 
From: Garner, Robert [mailto:rgarner(--nospam--at)moffattnichol.com]
Sent: Thursday, April 16, 2009 2:08 PM
To: seaint @seaint.org
Subject: RE: ACI 318 Appendix D
 
In our office, we through-bolt all our concrete anchors and avoid Appendix D entirely.
 
One engineer in our office has a detail where he attaches the heads of his anchor bolts to chains which are in turn fastened to large chunks of Iron dropped in the bottom of the concrete pour, all to avoid Appendix D.
 
"We don't need no stinkin' Appendix D".
 

From: Bill Allen [mailto:t.w.allen(--nospam--at)cox.net]
Sent: Thursday, April 16, 2009 1:26 PM
To: Seaint
Subject: ACI 318 Appendix D
 
O.K., I've beaten my head against the wall long enough. I've decided that a post-installed anchor won't work in tension for anything I design.
 
I feel better now.
 
 
T. William (Bill) Allen, S.E.
Consulting Structural Engineers
 
V (949) 248-8588 < /SPAN>F(949) 209-2509