Ravi,

I think your paraphrase might be misleading.  The actual text reads as follows:

Grade beams designed to act as horizontal ties between pile caps or footings shall be proportioned such that the smallest cross-sectional dimension shall be equal to or greater than the clear spacing between connected columns divided by 20, but need not be greater than 18 in........

I do not think your interpretation is correct.  They are describing a minimum value of clear spacing divided by 20 but cap the minimum at 18 inches not a maximum.

Thomas Hunt, S.E.
Fluor




David Topete <d.topete73(--nospam--at)gmail.com>
04/22/2010 02:20 PM
Please respond to seaint
To
seaint(--nospam--at)seaint.org
cc
Subject
Re: Geade beams per ACI 318-08 section 21.12.3.2





Sounds like a typo, but I don't have a copy of ACI 318-08.  Have they completely renumbered the sections?  In 318-05, there is no section 21.12.3.2...  I would guess that the minimum dimension is 18".  That would be silly to cap it at 18", don't you think?  If you have a 12" grade beam, then the stirrups are 6" out-to-out when you include 3" cover on either side...  Any reasonable plan reviewer could be this.

On Thu, Apr 22, 2010 at 1:47 PM, Vasu, Ravi <Ravi.Vasu(--nospam--at)jacobs.com> wrote:
List,

I have grade beams between pile caps in SDC D.   ACI 318-08 section 21.12.3.2 says,
the max. limit of least cross sectional dimension is 18 in.    Is there any reason

why the max. is set at 18 in.?  That means, we cannot have 24 in. or 30 in. (least)dimension?

I appreciate your help.

Thanks

Ravi Vasu


 
NOTICE - This communication may contain confidential and privileged
information that is for the sole use of the intended recipient. Any viewing,
copying or distribution of, or reliance on this message by unintended
recipients is strictly prohibited. If you have received this message in
error, please notify us immediately by replying to the message and deleting
it from your computer.




--
David Topete, SE

------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------