Charlie,

The values shown in Table 10-10 include the limit
state of bearing strength using Specification
formula J3-6a only. The limitations on the bolt
hole types for the Conventional Configuration SPSC
are stated to exclude long-slotted holes with slot
parallel to the direction of force, Spec formula
J3-6c.

If long slots are used, then the additional limit
state from formula J3-6c must be checked. However,
I have not found the bearing strength limited by
formula J3-6c on SPSC that are thick enough for
erection stability.

>From a fabricator/erector viewpoint, I have argued
against some of these limitations in Manual
committee meetings, but it seems there are too
many engineers on the committee who don't want to
see SPSC used at all.

Replied by:
Davis G. Parsons II, PE RA

-----Original Message-----
From: seaint-seaosc(--nospam--at)mail-list.com
[mailto:seaint-seaosc(--nospam--at)mail-list.com] On Behalf Of
Charles Canitz
Sent: Friday, January 11, 2013 9:39 AM
To: seaint-seaosc(--nospam--at)mail-list.com
Subject: Re: [SEAINT-SEAOSC] Fwd: Single Plate LST
Holes

Harold -

   Thanks again.

   This is a situation where the SEOR was
requiring a slip critical type
connection since the Steel Manual's single plate
prescribed "cookbook"
design procedure mentions only standard and short
slot type holes.

   I advised him that the Specifications did allow
loads applied normal to
the long slot but he kept circling back to the
Manual's Connections and
Shear sections.

Charles Canitz

-----Original Message-----
From: Harold Sprague <spraguehope(--nospam--at)hotmail.com>
To: seaint-seaosc <seaint-seaosc(--nospam--at)mail-list.com>
Sent: Fri, Jan 11, 2013 3:00 am
Subject: RE: [SEAINT-SEAOSC] Fwd: Single Plate LST
Holes

Charlie,
The snug tight condition would be a bearing bolt,
and you can use them in
the direction perpendicular to the slot within the
limitations in AISC 360,
 Section 10.  If you need to resist load parallel
to the slot, it would
have to be slip critical.  Again it is defined in
Section 10.

Regards, Harold Sprague

> From: canitzcf(--nospam--at)aol.com
> Date: Thu, 10 Jan 2013 15:42:35 -0500
> Subject: Re: [SEAINT-SEAOSC] Fwd: Single Plate
LST Holes
> To: seaint-seaosc(--nospam--at)mail-list.com
> 
> Harold -
> 
> Thanks.
> 
> ST = Snug Tight. Due to the long slotted holes,
I was wondering if the
> ST type connection was OK or if a slip critical
type connection is
> required for this situation.

Truncated 381 characters in the previous message
to save energy.

<http://cgi.mail-list.com/u?ln=seaint-seaosc&nm=davisp2%40att.net>

-----
No virus found in this message.

-------------------------------------------------------------------------
Post your message to the list by sending it to: 
   SEAINT-SEAOSC(--nospam--at)mail-list.com.

The email messages sent to the list will be saved in an archive on the World Wide Web.
These archives are located at:
    http://archive.mail-list.com/SEAINT-SEAOSC

To contact the list owner, send your message to:
   SEAINT-SEAOSC-list-owner(--nospam--at)mail-list.com.

5700 Ralston Street, Suite 300, Ventura, CA 93003

To unsubscribe, switch to/from digest, get on/off vacation, or change your email address, click here.
<http://cgi.mail-list.com/u?ln=seaint-seaosc&nm=seaintma%40euken.net>