Also, the guardposts are the kind that sit on top of the deck.  I hate those. 
 The support connections appear to penetrate both the deck sheathing and the 
 bituthene membrane.  On one of the photos (#12), you can kind of make out 
voids on the top edge joist where the guardposts would be.  Could that be a 
 source of water intrusion?  Just throwing that our there.

I too noticed that the balcony framing is not pressure treated.

This tragic event is so sad.  In my own assessment, I wonder what else can 
a structural engineer do to prevent this.  PT or steel framing?  Detailing 
with potential water intrusion in mind?

Ricardo G. Gonzalez, P.E.
C S W | S T 2
CSW/Stuber-Stroeh Engineering Group, Inc.
45 Leveroni Court, Novato, CA  94949
Civil Engineering ∙ Structural Engineering
Planning ∙ Land Surveying & Mapping

main: 415-883-9850          fax: 415-883-9835
direct: 415-884-6442        e-mail: RicardoG(--nospam--at)cswst2.com
links: Web Site ∙ Blog ∙ LinkedIn ∙ Facebook ∙ Twitter

“This message is intended solely for the recipient identified above and 
should not be opened, read, or utilized by any other party. This message 
shall not be construed as official project information or direction except 
as expressly provided in the contract documents”

-----Original Message-----
From: seaint-seaosc(--nospam--at)mail-list.com [mailto:seaint-seaosc(--nospam--at)mail-list.com] On 
Behalf Of Andrew Kester Sent: Wednesday, June 17, 2015 2:58 PM
To: seaint-seaosc(--nospam--at)mail-list.com
Subject: Re: [SEAINT-SEAOSC] Berkeley Balcony Collapse-Professional Photos

Hassan,
Thanks to you and Lisa for sharing those pictures. That is some camera, I 
have to get me one of those! Even though they were shot from across the 
street you could zoom in really close and see lots of detail.

Very clear to me there was very severe rot damage to the joists and the floor 
 sheathing. Specifically Photo 7 (9712), the second joist from the right had 
 much more severe damage to the top than the bottom, confirming the source 
of water was from the top. It appears the bottom of the second beam from the 
 right was swollen unevenly, and the deterioration to both of the beams on 
the right (severe swelling, possible separation of layers of wood) makes me 
 think they were LVL or similar engineered lumber versus sawn lumber.  Anyone 
 else seeing that? I haven't seen much engineered lumber rot damage but sawn 
 lumber doesn't typically swell and come apart in layers in my experience.

I don't see counter flashing, or flashing, but the flashing could be underneath 
 the membrane.

No roof over the balcony, never helps..

Truncated 1326 characters in the previous message to save energy.

-------------------------------------------------------------------------
Post your message to the list by sending it to: 
   SEAINT-SEAOSC(--nospam--at)mail-list.com.

The email messages sent to the list will be saved in an archive on the World Wide Web.
These archives are located at:
    http://archive.mail-list.com/SEAINT-SEAOSC

To contact the list owner, send your message to:
   SEAINT-SEAOSC-list-owner(--nospam--at)mail-list.com.

Sponsored By: Pacific Structural & Forensic Engineers Group, Inc. (PSFEG)

To unsubscribe, switch to/from digest, get on/off vacation, or change your email address, click here.
<http://cgi.mail-list.com/u?ln=seaint-seaosc&nm=seaintma%40euken.net>